changing medium voltage input #30
-
Hi PGM team, With my team I am writing a model to get insights in the flex control on the low voltage level part of the grid. We assume symmetric loadflow while in practice that is not the case. At the moment, we see that the results always give relatively high voltages (min voltage over all nodes over the year is around 240 and maximum is around 255 Volt). We see this for more runs for different msr grids. My questions to you are: I tried to look it up in the documentation but I could not find the answer to my questions. |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment 7 replies
-
Hi @willemijnbrus, @nitbharambe and @zhen0427 will schedule a meeting to discuss this in detail. p.s. the experimental feature release of automatic tap changer is ready -> this might help you :) |
Beta Was this translation helpful? Give feedback.
The temporary conclusion is to see if tap changer regulators are indeed present in the grid and implement them per the example notebook as mentioned by Martijn. And if there is something more needed than that we shall have to do a deeper dive.
The questions you ask additionally are good power engineering refreshers. Although all information might not be relevant, its nice to address them here:
Changing the
u_rated
is possible only for power flow calculations. And its effects are only all thep.u.
results. It does not affect the real unit results likeV
,A
,W
,Var
,VA
. If the user intends to do it, it should be done with a good cognizance of its effects. However this generally not recomm…